time2roll wrote:
I would not be concerned as long as the voltage is getting to 14+ by mid afternoon.
If the voltage stays above the green line... why is the controller not limiting the absorption time or going to float?
Maybe I am misreading the graph.
The battery Voltage has not reached the ABS set-point for 4 consecutive days.
The 10-day history if the ABS set-point(regulation) is shown in the graph below:

and the 10 day history of battery Volts is shown in the graph below

On the the days 5/4-5/7, the battery volts have been below the set-point(regulation) Volts. The controllers cannot begin ABS until the battery Volts reach the set-point Volts. Accordingly, Float cannot begin until the ABS has completed its daily-set-time in ABS.
IOW, the controllers were in Bulk for the last 4 days.
HTH;
John