Dutch_12078 wrote:
Gdetrailer wrote:
Pretty much ALL of the APC UPS versions are MSW, not sure about "Cyberpower" but I suspect they may also be MSW since they tend to be a lot cheaper than APC, if not they may be extremely cheaply built PSW and if that is the case I would take a APC over the Cyberpower.
APC has a number of pure sine wave models, mostly in the Smart-UPS series. The Smart-UPS 750VA (SMT750) is just one of them...
That is a PRO model marketed toward a server room which most folks would not buy since it is more expensive than most consumers would be willing to shell out.. Nor would most consumers find these in most retail stores.
That is why I mentioned "pretty much ALL APC versions are MSW".
Retail stores typically carry the lower end shoe box/power strip versions typically 450 VA.
Additionally the model you pointed out specifies
"Output Frequency (sync to mains)
50/60Hz +/- 3 Hz" which IS why you are able to get it to operate with a generator.. MOST of the consumer UPS units typically will not be able to sync higher or lower than 60 hz properly.
Additionally APC states
"Output Voltage Distortion
Less than 5% " which is NO BETTER than MOST GENERATORS..
From
APC WEBSITE HERESo, in the end, even a Sinewave APC UPS cannot provide any better sinewave than most generators since most generators also spec similar distortion specs!
The only real nice part of a UPS is to catch the in between time from when the power goes out to the point you get generator up and running.
Much less about "clean" power..
As far as sensitive electronics goes, SHOW ME SOME REAL LIFE EXAMPLES of these so called "sensitive to dirty power electronics"..
I have run pretty much anything I could get my hands on over the years and have not had any thing blow up or burn up or malfunction from MSW UPS units and or portable generators..
One would think that TVs, stereos, sat equipment and PCs are "sensitive", they are not, not even a little bit..
Modern day TVs, sat and PCs ALL use switching power supplies, those supplies rectify the line input to DC, then run that DC through a high frequency chopper the chopper output goes through a high frequency transformer, the output of the high frequency transformer is rectified and filtered to DC..
NOTHING in a switcher is "sensitive" to dirty power since the initial input stage is rectified to DC AND BRUTE FORCED "filtered" via a high voltage capacitor (typically 470 UF at 400V).. The chopper never sees any "dirty power".
Switching power supplies are not sensitive to frequency as they are designed to be used with 50hz - 60 hz. Pretty much nearly all switching power supplies now days are "universal" for input voltages, most are designed to operate from 100V AC to 250V AC.. Very few are for 120V only or 120/240 MANUAL switchable now days but even those had a wide range of voltage they can accept.
OP does not "need" UPS units to "clean" the generator power..
The only reason one would WANT a UPS would be to provide backup power until the generator has started and stabilized.
But OP does need to be aware, NOT ALL UPS UNITS will be able to sync to a generator and that is what I was getting at.