You have 2 problems:
First you have a ground fault that would immediately trip a GFCI if you plugged into one. This needs to be fixed since it compromises safety.
Second: You have a open ground allowing voltage on the ground components. They should all be securely bonded to the ground wire all the way back to the CG/home service panel where the ground, neutral and earth ground are bonded. This is potentially a very serious issue as someone could get hurt.
Recommend that every RV periodically plug into a GFCI plug and check all equipment for safe operation. For a 20A GFCI plug wait for the battery to charge (or turn if off) and then test each appliance.
There are many posts on how to find the problem area.
First you have a ground fault that would immediately trip a GFCI if you plugged into one. This needs to be fixed since it compromises safety.
Second: You have a open ground allowing voltage on the ground components. They should all be securely bonded to the ground wire all the way back to the CG/home service panel where the ground, neutral and earth ground are bonded. This is potentially a very serious issue as someone could get hurt.
Recommend that every RV periodically plug into a GFCI plug and check all equipment for safe operation. For a 20A GFCI plug wait for the battery to charge (or turn if off) and then test each appliance.
There are many posts on how to find the problem area.