After a period of non use one does not purge air from propane system.......one establishes flow on a static system and places a demand on LP Regulator.
It's as simple as that.
......
Not that simple. On mine there IS a flow when the burner valve is first opened (as indicated by the match flame being blown about) but ignition does not occur for a minute or more after that flow starts.
That is because LP regulator has opened to provide 0.4 psi in downstream system......but then closes back down until demand is required.
Upon demand the little bit of propane in system is not sufficient for ignition (or maintaining ignition ) until higher flow is established, which happens when reg senses demand and drop in line pressure.
Lighting off stove top burners helps establish flow and demand which places regulator fully in service vs static state when not being used.