OldSmokey wrote:
BFL13 wrote:
"- battery V drop under load is halved on a % basis at 24v"
Is that true? It might be halved or doubled as such, but I would think on a Percentage Basis it would be the same. Please elaborate--my brain quit :)
assume T105RE with internal resistance of 0.001 Ohms per cell and 1200 Watt load
for 12V we have 6 cells so 0.001*6*100 A = 0.6 V
0.6/12*100% = 5 percent drop
for 24V we have 12 cells so 0.001*12*50 A = 0.6 V
0.6/24*100 = 2.5 percent drop
Wait a sec! My 12v system has 0.6v drop when pulling 120 amps from the 450AH, whatever , bank.
It does not matter what the starting voltage is, it drops 0.6v. so from 12.5 it drops to 11.9, and from 12.2 it drops to 11.6 (as seen on the Trimetric) so right away the percentage is different within the same "12v" system. the inverter will alarm at 11v--it doesn't care where you started from.
If I had a 24v system, it would pull half the amps, but the burning question is---what is the 24v inverter alarm at? Is it 22v no matter what? I don't know, so I am asking about that for a percentage comparison.
EDIT-Ha! his 24v inverter will alarm at 22v, same as a 12v will alarm at 11v. So how do you get a percentage difference for low voltage out of that?