disckDoctor your wiring diagram is wrong you have a dead short on all your batteries
there are ONLY (4) interconnect wires used/needed
only one positive to negative connection in each pair
(2) batteries side by side positive to neg
is going to blow up
there are ONLY (4) interconnect wires used/needed
only one positive to negative connection in each pair
(2) batteries side by side positive to neg
is going to blow up
DiskDoctr wrote:2oldman wrote:
For a 1200w appliance, this is what the approximate amperages to the inverter look like in your setup:
Before we get too involved in this, please share with us what will be the largest loads on your inverter.
Okay, so this is my planned battery wiring diagram.
Each of the 6 wires would be about a foot and would carry up to 100 amps each, correct? They wouldn't have to be doubled, right?
Then the two leads from the center to the right side of the drawing would have to carry 400 amps and would be...doubled 2 AWG (not 2/0), right?
Microwave 13amps is biggest load. I was trying to account for startup surge ;)