RV generators have the neutral and ground bounded (as do shore power connections), so your EMS is probably faulting when it doesn't detect that bonding.
Your generator may have a way to connect a bond strap, or you can buy (or build) an RV bonding plug to plug into one of your generator's 120V 20A plugs:
Southwire CompanyNeutr al-Ground Bonding Plug
Most 30A->50A adapters will connect both 50A hots together (so you get power on both hots), so it's possible that your EMS is complaining about that, but it's most likely the neutral-ground bond.
Your generator may have a way to connect a bond strap, or you can buy (or build) an RV bonding plug to plug into one of your generator's 120V 20A plugs:
Southwire CompanyNeutr al-Ground Bonding Plug
Most 30A->50A adapters will connect both 50A hots together (so you get power on both hots), so it's possible that your EMS is complaining about that, but it's most likely the neutral-ground bond.