BFL13 wrote:
I had this problem before (two years ago) and got some help on here with it all, and swapped some parts from a 111 I got off a guy. Eventually I got a 111's board from a 98 MH being parted out and that got it working right. New burner head (old one had screen rusted out) Now it is starting to act up again.
ISTR I swapped the squirrel cage fan-- found out how to get it off here--that was to try a new limit switch you have to get the fan off first to get at.
The one in there now is metal and heavier than the plastic one I have in the spares box. Can't remember which is the 11 vs the 111's. Anyway it spins ok, and the delay for burner on at the start after fan runs and then at the end for fan to stay on after burner off is working right.
It is just the burner cutting in and out when it should just stay on.
I can haul the burner end out again and check the wiring for the flame sensor and however it is grounded. Is there a way to check the voltage with it out? Maybe turn the Tstat to on? Is there any voltage when there is no gas?
Wiring diagram can be found
HERE on page 9.
Burner cutting in and out..
Partial blockage of the burner orifice causing flame to not be correct size and position.
Flame detect not positioned correctly in the flame.
Flame detect grounding issue.
Fan running too slow or too fast altering flame position.
Bad control board?
Overheating?
Sticking or bad gas valve?
Flame detector is a dual purpose device, it is used to spark ignite the gas in the burner and once the gas has ignited, the probe now operates as the flame detection system.
As flame detector, the control board will place a small voltage on the probe. When proper ignition has occurred the probe should be inside the blue part of the flame. The blue part will conduct a small amount of electricity generating a small current that flows from probe to burner. Control board monitors the current drawn on the probe if no current or wrong current is drawn the control board will close the gas valve.
This is known as flame ionization detection, some times called flame rectification since the current flow is one direction only..
HERE is a good write-up on this type of flame detection with some troubleshooting info.
Ground is typically established through the burner assembly and burner assembly should have a ground connection to the 12V negative and control board. If in doubt that the flame sensor or burner may not have a good ground established, you can add a grounding wire to the burner to a known good ground to see if that helps.