wa8yxm wrote:
As I understand it the parallel link has only two wires to each generator. Thus you will need to bond at the 30 amp outlet in the P-link.
I don't know about the Champion paralleling system, but the Honda paralleling system has 3 wires between the generators. It bonds the Hot, Neutral, and Ground. The bonding plug can go in any outlet as long as that outlet is on one of the generators.
And no, you do not need a bonding plug on each generator. One, on either generator, is sufficient.
ON EDIT: I just looked up the Champion parallel kits. They, also, have 3 wires. They have Hot, Neutral, and Ground.