HI Rmc
I am happy to help but need the detailed info asked for earlier
To directly answer/comment on the above post
The TS-RM-2 RJ-11 connection uses the Meterbus communications protocol a completely different and isolated protocol (using the MPPT 60) than the Ethernet IP protocol I believe you are trying to connect to - The TS-RM-2 has zero affect on the RJ-45 communication from the MPPT-60.
Have you connected to the controller with a serial cable?
What exactly does the "Network communications" configuration page of the MSView configuration wizard show?
I am happy to help but need the detailed info asked for earlier
To directly answer/comment on the above post
The TS-RM-2 RJ-11 connection uses the Meterbus communications protocol a completely different and isolated protocol (using the MPPT 60) than the Ethernet IP protocol I believe you are trying to connect to - The TS-RM-2 has zero affect on the RJ-45 communication from the MPPT-60.
Have you connected to the controller with a serial cable?
What exactly does the "Network communications" configuration page of the MSView configuration wizard show?