red31 wrote:
• Nominal operating cell temperature (NOCT): 45±2?
looks like that panel gets 25C warmer with 80% sun.
The coefficients are used with temps different than 25C STC
http://pvcdrom.pveducation.org/MODULE/NOCT.htm
Thanks for the link!
Red,
If Tair = 30C, and NOCT = 45C, and S = 80, it gives a result of 55C. Would this be the cell temp for a fairly well ventilated, average panel, at 30C ambient, then?
If so, 55C - 25C = 30C, so the panels I'm considering would lose about 67.5 watts, at 30C ambient? ( 0.45% x 30 = 13.5% x 500w = 67.5w )
(In that case, the peak amps would likely be in the 26a range :))