I have a 2005 Mandalay with a Dometic refer, model NDR1292. During colder temps outside my refer turns off. Once the outside temps gets back into the higher 50s or 60 d range, the refer turns on. I don't believe it's an electrical issue. Any help/suggestions? Yhanks

14 Replies

  • Clarify. Is the refer eyebrow control panel turning OFF (no indicator lights) or the refer just does NOT cool? Doug
  • Have you tried turning 'Low Ambient Switch' ON when outside temps drop below 50*F?

    You have 2 switches under top panel (open door and look up)
    One is a 'Climate Control Switch'----used during high summer temps/humidity. It energizes a 12V DC heater strip to help keep condensate from occurring (it pulls 12V DC continuously)

    The other is 'Low Ambient Switch'----used when outside temps drop below 50*F.
    It keeps the interior light on when door is closed.