TenOC wrote:
This is why I NEVER put plastic blocks under my stabilizing jacks. It may not be the best ground, but I want metal stabilizing jacks on dirt..
Metal jacks on DRY "dirt" does nothing at all to prevent shocks.
One would have to SOAK AND SATURATE the dirt with loads of water with minerals to even get a tiny effectiveness.
Then you would have jacks that simply sink right into the MUD.
Starting with a KNOWN GOOD electrical service entrance ground connection is the BEST WAY to prevent electrocution. Modern day electric service entrance requirements is at least TWO SIX FOOT ground rods driven below the surface of the ground and separated by no more than six feet apart.
The ground rods must be bonded together then the ground wire must be connected at the service entrance box and the neutral and the ground most be bonded together INSIDE THE SERVICE ENTRANCE BOX.
That puts the neutral and ground wires run throughout your home at the same ground potential.
Many older homes and campgrounds with old electrical systems are grandfathered and may have only ONE ground rod or worse, use only the water line to provide a ground connection.
A RV breaker box however is considered a downstream breaker panel or sub panel and is treated a bit differently when it comes to the ground wire and neutral wire.
A sub panel MUST have totally separated ground and neutral bus bars and depends on the connection via the shore cord from your home or campground outlet/panel to provide the neutral/ground bond.
The OP simply needs to do some easy trouble shooting working back to the service entrance.
Start at the trailer breaker panel, make sure the panel is wired correctly, the neutral and ground from the shore cord MUST be on completely separate bus bars.
IE green ground wire from shore cord must be connected only to bare or green ground wires on one bus and the white from the shore cord must connect only to white wires on one bus only.
The black wire from the shore cord must connect to the master breaker (in the case of 50A Black and Red of the shore cord must connect to the master breaker).
If all that checks out then proceed to check the shore cord with an ohm meter to verify no broken ground connection exists on the shore cord and plug.
If that checks out, check to verify the adapter plug if used to adapt trailer to 15A/20A home outlet has no broken connection for the ground.
Verify any extension cords if used are wired correctly and no broken or switched wires exist on those cords.
If all of that checks fine then move to testing the home or campground wiring to verify no switched wires or missing ground..
Now if the OP is using a generator and is finding a hot RV skin that is different problem called a floating ground.. In that case this is to be expected since the generator whether a portable or built in type has no way of being connected to earth ground.. Powering a RV via an inverter can also show a voltage and is also expected due to no earth ground connected to the inverter.