ov10mech wrote:
The question is - is it possible to somehow combine these two power sources into a single 50 AMP input?
A true 50 amp service, NO - the reason being that so-called 50 amp RV service is actually 100 amp service - i.e. 50 amps across each of 2 legs. With an adapter with one leg pulling from 30 amp service and the second leg pulling from 15 amp service your total draw will be limited to 45 amps, not 100 amps.