Chris Bryant wrote:
The only problems I have with tandem breakers is where both sides have a large load on them- often the 30 amp service coaches will use a 30/20, with the 30 being the input, and the 20 being the air conditioner- these will get pretty hot.
Yes, this is correct. ^^^
Some electrical inspectors don't like tandem breakers but they are CSA/UL listed so there is NO code/standard problem using them. These are used everyday, everywhere, all the time without issue. The only potential downside is the heat from an adjacent breaker in a "tandem" breaker or in the panel. Circuit breakers are thermal/magnetic devices and heat from an adjacent breaker can possibly affect it's operation. If mutual heating from an adjacent breaker is a problem, you can always rearrange circuits. A typical tandem breaker is in the photo below. Each half is sometimes called a 1/2 slot size breaker. Note the rear of it only has one stab that goes onto the bus bar.
Square D used to make a 1" wide 2x15 amp QOT breaker that was called piggyback style because it had handles that were end to end instead of side by side. Not sure if it is still made or anyone else does.
The only way you can use a 2-pole breaker in an RV panel is if it is 120/240 volt as in a 50 amp panel and will take a 1" space. If you run out of breaker spaces in a panel you can typically replace a standard 1" wide breaker with a tandem breaker. The only exception would be if you would be adding too much load to the supply wire/cable (feeder) to a panel and it's breaker.
CJW8 wrote:
Just install your tandem breaker but don't put your two heater circuits on it. Move other loads around so that it will be more balanced. It will never be perfectly balanced. Your microwave and coffee maker only run for a brief period of time.
Agree. ^^^
Know that a circuit breaker does not trip the instant it reaches it's rating. It can run for a quite a while with a small overload and will allow for a coffee maker or MW to run fine. You may or may not benefit from trying to balance loads. You could easily check the ratings of your various appliances that could be running at the same time as the heaters and see how that compares to the 50 amp breaker rating by calculation alone. If you end up tripping the 50 amp breaker in your panel or a pedestal, you'll know for sure you need to juggle some circuits around - no harm done. Breakers are pretty cheap, you could also just balance the loads from the start. Low voltage can make quite a difference too. A typical time-current breaker graph is below.