Furnace Burner Cycling at startup

My 2016 Montana High Country has an Atwood/Dometic furnace, model AFMD35131-A. Whenever I turn the furnace on (or it comes on based upon the thermostat setting), the burner will cycle on and off several times before remaining on. Here's the sequence:
-the furnace blower comes on immediately
-the burner will ignite after 30 seconds or so (normal operation)
-the burner will shut down after 5-60 seconds of operation
-the burner will re-ignite after being off for 10 seconds or so.
-the blower stays on during this cycling
-this cycle will repeat itself 1-5 times before the burner stays on and heats the camper to the set temp on the thermostat.

My propane tanks are approx 50% full. Could being at an altitude of approx 9,000' be a factor.

Any suggestions? Thanks.
  • OP...you have enough discharge ducts.
    How is airflow from each register...lacking could be sign of collapsed duct

    How is return airflow. Nothing stacked up next to furnace OR obstructing return air??

    Check exhaust ......obstructed will cause heat build up (mud dabbers. nests)

    Propane pressure.
    Turn ALL stove top burners on HIGH one at time.'
    Do flames recovery quickly when another is lit?
    Are all flames same....height/color?

    With flames on ....turn furnace on.
    Get same short cycling?
    Do stove top flames diminish or stay steady?
  • Could be the flame sensor - if it's not in the right location (bent mounting bracket?), it could take a couple of cycles to heat up so the controller knows the flame is actually coming on.
  • Thanks for all the feedback. Here's a followup.

    - the led on the circuit board is not flashing.
    - the specs on this furnace call for a min 36 sq inch of discharge area. My furnace has 4 - 4" flexible ducts. The furnace is installed in a vertical configuration with two 4" discharge ducts on the top and two 4" discharge ducts on the rear, plus a 2" discharge duct on the rear. Each 4" duct provides 12 sq inches. So, it appears that I have 54 sq inches of discharge area. All the outlet registers are full open. Air flow should not be an issue.
    -Someone mentioned that it could be thermostat related. More information on this please.
    -Today I made a request to Dometic for suggestions on this issue. No feedback from Dometic as of this posting.

    Thanks again for all the responses.
  • sgip2000 wrote:
    Ever since Dometic bought Atwood, Atwood has gone to ****. Cheap, Chinese junk now.

    Explain your expertise to state such ignorant nonsense. Doug
  • sgip2000 wrote:
    Ever since Dometic bought Atwood, Atwood has gone to ****. Cheap, Chinese junk now.


    Check out what is manufactured in Greenbrier TN
  • Ever since Dometic bought Atwood, Atwood has gone to ****. Cheap, Chinese junk now.
  • I agree it sounds like it is cycling against the high limit switch.
    Probably need to add one or two additional ducts to get more airflow... unless you can repair the existing ducts to flow much better.

    Mine did this for 8 years. I had tried to open the collapsed and poorly installed ducts for some time. Finally gave in and added two more 4" round ducts through the cabinet. Works perfect and tons more heat.
  • Sounds like it is operating off of the 'high temp' switch---called 'limiting'

    Temp comes up to fast a rate of increase..furnace overfiring...high temp switch opens shutting down DC to circuit board. Fan continues to run...high temp switch cools/closes/DC back to circuit board/t-stat still calling for heat so burner fires.....cycle repeats

    Causes:
    Blocked ducts, too many registers closed/obstructed ----resists air flow
    Restricted return air -----minimizes amount of air back to furnace
    LP System Pressure.......too much fuel/overfiring
    Defective high temp limit switch.....190*F switch #31091

    If you remove outside access panel you should be able to see the LED on the circuit board
    1-Flash with 3 second pause.......Limit switch/airflow issue



    AFM Series Furnace