Fusing REQUIRED?

consider 6A Isc panels with 10g wire

parallel 3, 1.56 x 6A x 2 = 19A

parallel 4, 1.56 x 6A x 3 = 28A

with lower amp panels, one does not need to fuse until 10g rating is exceeded by the number of paralleled less one?
  • 2oldman wrote:
    Few of us fuse panels. Run them in series to avoid amperage issues.

    Full sun always?
  • I'd suggest to install a manual trip circuit breaker between panels and charge controller. You may need to interrupt power from the panels at some time and a breaker with manual trip is made for that.

    Bussmann manual reset CB
  • Fusing makes for more connections, and in turn more resistence, not to speak of more places for corrosion.
    No need to fuse panels, period !
  • Few of us fuse panels. Run them in series to avoid amperage issues.
  • Technically each panel has a fuse rating. 15 amps is typical but check the specs. To protect the panel during some internal short you should have fuses on each panel as they enter the combiner box if the total exceeds the fuse rating. Most people seem to skip this.

    For the main feed down to the controller there is no fuse needed as the wire chosen would always have the ampacity of the full solar array. Although some install a breaker or switch to cut power for easier service. Removing a fuse is also an option to break the circuit.
  • Are you asking if larger wire means you don't need fuses? Not a solar expert, but I'd say no.