Bill,
To me, this is more than a hypothetical question. The answer is that it will probably start and cough off very shortly there after. This is why emergency generators have a load-delay. The diesels are kept warm and do not have much problem but still need 15~30 seconds to get the lube oil up. Most spark ignition engines need a moment to get the mixture right.
There was a time that I watched a fellow camper at a rustic campground beat himself up trying to run a generator. He would rip the rope and it would fire and run a bit, stumble and then die. Finally, I had to go see what his problem was. (I am a ship's engineer by trade as so well versed in engine stuff.)
When asked if it was unloaded and he said it was and the breaker was visibly open. I touched it and the toggle was loose. He said it has failed and was not common breaker, so a "friend" had by-passed it. He said everything inside the trailer was off. I suggested that he unplug the shore power cable and try. This resulted in a running machine. He didn't want to reconnect it hot. (There is some possibility of damage is there is some load.) Well, there was load. When he restarted, the engine - now warm - bogged until it could catch its breath. I suggested that he go inside and see what was on that should not be.
He was kind of embarrassed when he came back out. The water heater was on..... It was a 2K machine and the heater was 1.5, but more than the cold machine could manage without a running start.
There you have a definitive case.
Matt