BFL13 wrote:
...
Once I found that cut and got it all proper, no more GFCI popping from that cause. The receptacle was ok, it was that white wire touching a grounded metal part behind it.
If that metal box were not "grounded", would the GFCI still pop?
OR --if there is no ground, how can you have a "ground fault"?
Most likely it would trip, but not due to a current imbalance between the hot and neutral lines. Modern GFCIs have special circuitry to detect faults between the ground and neutral lines downstream even absent any applied load (and thus no current imbalance). If the box is connected to the GFCIs ground, which it presumably is by virtue of the GFCI's mounting screws, then it would trip for that reason.
Likewise, if the ground lead is intact back to the service entrance where it is bonded to neutral, a fault path for the current exists whether or not it is properly earthed.
In the case of an RV with a missing ground connection in the shore power cord, a hot to ground fault would in theory not trip the GFCI as there is no fault current, at least until someone walks up and mounts the entry steps with bare feet. At that point, a GFCI would trip and stop a nasty shock or worse.