BB_TX wrote:
But the description describes a "grounded neutral" which goes back to the question of how can you have a "grounded neutral" when there is no ground connection at all to the trailer. Current does not flow into an open ended wire. And an ungrounded frame is effectively an open ended conductor.
It's a question of semantics, really, at this point.
The GFCI will detect a short between the neutral wire and the ground wire downstream from it. Whether or not either one connects to earth is immaterial for that detection. It's called a grounded neutral because the neutral wire is connected to the ground wire, using the conventional names for the wires. (Just be glad they didn't go with the terminology of the NEC where it calls them the grounded conductor and the grounding conductor! They're accurate enough descriptions, but it does make understanding what is going on rather tedious at times.)
If the GFCI in question is feeding the RV electrical system as a whole, and the ground lead between it and the RV is broken, then of course it won't trip because of a neutral to chassis ground fault in the RV, as it doesn't see its ground and neutral lines bridged together. If it's in the RV, then it matters not one whit whether the ground (or neutral, really) is tied to earth or anything else; the GFCI can detect an unacceptably low impedance between the two wires, and trip because of it. In this case, the ground lead is not open ended--it goes back to the GFCI.
Nothing in a GFCI's operation has anything to do with stuff being earthed or not.