OK, I turn main 50 amp breaker in box OFF, thinking I could turn on circuits until I find one that pops outlet. Still, the outlet GFCI I am plugged into pops
Your issue is between the GFCI Outlet and your MAIN AC Panel
Adapters, Extension cords, main power cord, AC REEL (if equipped) ATS
Anyone of those could be 'leaking'....only takes a few milliamps on Ground circuit to trip a GFCI
Leave RV Main 50A CBs OFF
Reset the GFCI
Then plug in each item (adapter/cords etc) one at a time
IF it only trips when you plug in RV Main Power Cord then you will need to check cord, REEL (if Equipped) and ATS more closely
Could try replacing the GFCI Outlet ...they do get weak
***Did Dealer do ANY electrical repairs/work???
If YES....recheck that work
OK, I turn main 50 amp breaker in box OFF, thinking I could turn on circuits until I find one that pops outlet. Still, the outlet GFCI I am plugged into pops
Your issue is between the GFCI Outlet and your MAIN AC Panel
Adapters, Extension cords, main power cord, AC REEL (if equipped) ATS
Anyone of those could be 'leaking'....only takes a few milliamps on Ground circuit to trip a GFCI
Leave RV Main 50A CBs OFF
Reset the GFCI
Then plug in each item (adapter/cords etc) one at a time
IF it only trips when you plug in RV Main Power Cord then you will need to check cord, REEL (if Equipped) and ATS more closely
Could try replacing the GFCI Outlet ...they do get weak
***Did Dealer do ANY electrical repairs/work???
If YES....recheck that work