MrWizard wrote:
Start generator…all good. See GFCI in coach in bathroom popped. OK, I reset it thinking somehow that had something to do with issue. Shut generator off and plug in again. GFCI pops again that I am plugged into. (Also, GFCI in coach pops.)
This the key point
Gfi for house trips, RV bathroom gfi trips
When shore cord is plugged in
Nothing trips when on generator, RV bathroom gfi Does Reset on generator power
Problem is between ats and stick house gfi used for shore power
ATS does switch hots and neutral
Neutral leak is NOT present when using generator
Either that or the generator isn’t bonded. If it isn’t bonded, there is no loop formed between neutral and ground even with a downstream neutral/ground short.