GFI Problem

I am trying to figure this problem out and don't quite know where to look next. When I plug in to a campground outlet that is GFCI protected, as soon as my surge guard kicks in the GFI protector on the post or otherwise protected outlet will trip. I have no problems in the coach or with any of the protected circuits in it. The voltage leak has to be on the coach side of the surge guard. Where do I start to look?

38 Replies

  • Have you had this problem on more than one GFI? GFIs do go bad.
  • When you turned all the breakers off did that include the Main Breaker(s) also

    Turn ALL breakers OFF and then see if GFCI still trips. If it does...problem is between pedestal and Main Panel

    Bad adapter, bad cord, bad connections in cord, bad wiring.......

    IF it doesn't trip then turn Main Breaker(s) ON and repeat.
    Then one breaker at a time.
  • OK. So I shut off all the breakers and it will still trip the GFCI. So I guess the problem must be between my hardwired Surge Guard and the Main Breaker box (which is about 2 feet of wire)? I installed the SurgeGuard myself. I know that the common and the ground are separated. My coach is wired for 50 amp with a 50 amp Surge Guard, but I have only 1 AC unit so I almost never plug into 50 amp. I prefer to use the much smaller 30 amp cord. Anything there that I am missing?
  • We see the same thing if we plug into any, not just campround, outlet that is GFI protected. I would be interested in an explanation too. I was previously told that it was because the RV does not have a ground to earth that the GFI is looking for. :h
  • Bobbo's avatar
    Bobbo
    Explorer III
    Somewhere in your RV there is a NEUTRAL to GROUND short. It could be anywhere.

    Disconnect the RV from all power. Remove all NEUTRAL wires from the buss bar in the breaker box. Plug back in. If it trips, the problem is between the Surge Guard and the breaker box.

    If it doesn't blow, disconnect, reattach one NEUTRAL wire, reconnect. If it blows, that is the circuit with the problem. If it doesn't blow, repeat process till it blows.

    When it blows, trace that NEUTRAL to see where it connects to ground. It could be in a stripped/pinched/punctured wire, an outlet, an appliance, anywhere.
  • Turn off all your breakers in the RV panel. Plug in the GFCI shore power pedestal. IF it does NOT trip, then your shore Cord/Transfer is OK. Turn on the 50 or 30 amp MAIN breaker in your breaker panel. If it does NOT trip the GFCI, then turn on 1 Breaker at a time until the GFCI trips. Once you have determined which breaker when turned ON trips the shore GFCI. either run your APU and then determine what outlets/appliances are ON that circuit. Then trace and disconnect each appliance or circuit 1 at a time until you find the problem. Doug
  • I would get one of these circuit analyzer, plug it into an outlet in the RV and see what it shows when the RV is plugged into a non GFCI protected outlet.

    It is often the fault of water in one of the exterior outlets.
  • It could be a faulty appliance. I would start by unplugging everything I could. Shut off the hot water heater and refer. Then try it. It could be the heating element in the refer or hot water heater.

    The GFI trips because of a faulty grounding situation, not an overload.

    If it still trips the power distribution panel may not be wired correctly. The white (neutral) and green (ground) wires should Not be hooked together. I have seen that on other units.

    Might get an electrician to help you if you are not experienced.

    You may call me if you wish.
    I am an electrical troubleshooter.