PT you might be right about the victron monitor
But that will not compensate for a sulphated battery system
That no longer has the capacity the monitor is programmed with, 12.1v is Not the correct voltage of a system at 78% SOC, the SOC says he used 22% by counting the power used, but the volts reading indicates 50% SOC,
The batteries real capacity is only HALF of whatever the monitor is programmed for, time for some new batteries , and a re-examination of the use/recharge regimen, maybe there is a bad cable or dead battery, and he is only using half of the installed batteries, or the cables are good but the batteries are heavily sulfated
But that will not compensate for a sulphated battery system
That no longer has the capacity the monitor is programmed with, 12.1v is Not the correct voltage of a system at 78% SOC, the SOC says he used 22% by counting the power used, but the volts reading indicates 50% SOC,
The batteries real capacity is only HALF of whatever the monitor is programmed for, time for some new batteries , and a re-examination of the use/recharge regimen, maybe there is a bad cable or dead battery, and he is only using half of the installed batteries, or the cables are good but the batteries are heavily sulfated