odenwell wrote:
Just as a point of reference, my Honda 2200 has no issue pumping out all 90 amps using my Iota 90 amp charger. Verified using a Victron bmv712 battery monitor on my AGM batteries. It is not running at 100 percent, either.
Do you have the 90 or the 90-X ? I see a typo in the 90-X where they said 30 where they meant a 20a receptacle.
https://www.solar-electric.com/lib/wind-sun/DLS-90-specs.pdf
I think it means the 90 and 90-X do not have PF correction, so expect 0.7PF.
The Honda 2200 is rated for 1800VA continuous vs 1600 for the 2000