marc71 wrote:
I have two Honda EU2000 generators that we occasionally operate in parallel operation. The owners manual states to disconnect the cables when not running both generators. I've noticed other campers running one generator while the cable was still connected to the other. To clarify, the camper is plugged into the 30amp plug on the generator and it's not running, the campanion generator is running. Thoughts on this?
Your statement is a bit confusing. When you refer to COMPANION GENERATOR, you must be referring to the accompanying generator as a support for the other standard 2000i unit to handle a bigger load.
However, (as you stated) only the companion is running and the 30 Amp plug is plugged-in to the standard unit 2000i.
The standard 2000i doesn't come with the 30 Amp plug. . . only on the 2000ia Companion Model. Note the difference between the 2000i and the 2000ia.
Now, to give you a bit on how these inverter generators work:
The old technology and most older RV generators (and the cheap ones) are equipped with non-inverter type. They generate power and deliver the energy direct from the stator. The inverter type generates DC first and then inverted to AC, hence the word inverter.
This provides better control by controlling the DC portion and also convenience for paralleling operation.
The manual tells you to disconnect the parallel cables when using only one. This is just as logical as one can get doesn't it?
By running only one (assuming you have the RV plugged-in to the 30 Amp twist lock) and the parallel cables are connected to the non-running unit, you are simply energizing the armature to create magnetic flux within its winding. Without the generator spinning, it will not make electricity because you are not breaking the magnetic flux for the stator to create energy.
Leaving them hooked up will be an added demand from the running unit and will shorten the running time of the generator.