DrewE wrote:
127V sounds perfectly reasonable to me. Normal tolerance for utility power is +/- 5% of nominal, or 114V to 126V. It sounds as though you're within that range to the precision of your measuring equipment. It may well be that the UPS has some other "reason" to not like the generator output--maybe it's looking for a ground to neutral bond and not finding one?
This........It may well be that the UPS has some other "reason" to not like the generator output--maybe it's looking for a ground to neutral bond and not finding one?
Yup. If you bond the neutral, all will be fine.