mstoetz1 wrote:
I have a new Honda Inverter eu3000is generator and noticed that when we use it, the UPS we have connected to it doesn't like the honda's output voltage and won't switch off battery.
I measured the Honda output, and its 127volts which seems a bit high for a "load voltage". It appears the voltage doesn't change much between no load and load.
I would have figured the honda inverter generator would have a nice clean regulated 120v output.
Does anyone know if this generator should be outputting this voltage?
Just wanted to be clear, do you have a UPS or an EMS (electrical monitoring system)? They are two completely different animals.
I would concur with some of the other posts, this is most likely an unbonded neutral-ground issue. It could be something else, but since you have voltage present, I would start by resolving the neutral-ground bonding.