SoundGuy
Dec 25, 2016Explorer
road-runner wrote:
The answer would seem to be on page 14 of the user manual:
"Wiring faults detected include missing ground, hot-neutral polarity reversal, and overloaded neutral circuit".
You probably don't have a missing ground, the UPS has no way of knowing, but it thinks you have a missing ground. Try the bonding plug. You still won't have a ground, but the UPS will think that you do.
Exactly ... no different than feeding a floating neutral output from any Honda EU series genset to any EMS with open ground detection which interprets that floating neutral as an open ground. G-N bonding the genset output will solve the problem.
Having RV issues? Connect with others who have been in your shoes.24,413 PostsLatest Activity: Aug 12, 2013