Forum Discussion
Dusty_R
Jan 26, 2016Explorer
If you add a panel breaker or fused disconnect you then need to have 4 wires in each conduit to where ever they are feeding.
Assuming it is 120/240 volt.
2 hots
1 neutral
1 ground
Even through the neutral and ground are one and the same at the meter and first disconnect, they are separated after there.
If you add just one breaker and receiptal then the rest can remain as they are. Most likely 3 wires.
Dusty
Assuming it is 120/240 volt.
2 hots
1 neutral
1 ground
Even through the neutral and ground are one and the same at the meter and first disconnect, they are separated after there.
If you add just one breaker and receiptal then the rest can remain as they are. Most likely 3 wires.
Dusty