time2roll wrote:
lafester wrote:
time2roll wrote:
Is the inverter feeding the main panel or just a branch circuit after the panel?
I am pulling the outlets off the circuit to be powered directly by the inverter/transfer switch.
OK so just remove the branch romex from the panel and connect to the inverter output. Get a new piece of romex and connect that spot in the panel to the inverter input.
Done. No converter relay, no bypass, nothing else to worry unless there is something actually on that circuit. Power will not go backward to the main panel. The bypass is the internal transfer switch.
Yes, already removed from the plan. Now looking for a possible way to bypass the inverter in case it fails and I still need shore power. Thanks for the input!