prier5 wrote:
The 100 amp is just for starting the charge rate is 30amp and automatically switches to maintenance mode.
That will make a difference on your generator, where a 100amper would need a big input that the gen might not have. I have a 100amp PowerMax charger but it is power factor corrected so it doesn't take so much to run it.
It should take your 30amper about three hours and fifteen minutes to do a 50-90 on the pair of 6s. If you had a second 30amper and used them both at once( if the gen can handle both) you could knock an hour off that time to do the 50-90