Need help diagnosing roof A/C

On Edit: Problem successfully diagnosed, last post here.

My roof air Conditioner / Heat Pump does not cool or heat. It is a three year old TT with a Dometic low profile Penguin II High Output 15K BTU with heat pump. Model number 651816C851J0. The thermostat is the CCC II digital.

The fan and compressor start and run, both start and run capacitors for the compressor both test within spec. The sticker on the compressor reads, RLA cool 13.4 and RLA 12.2 heat.

The compressor pulls 10.5 amps per my clamp over meter on both cooling and heat pump after running 30 minutes on each. My supply voltage maintains 115 or more.

There are slight oil stains on some of the solder joints of the Freon tubing, but not much, (normal?)

Manufacturing stickers on the AC frame under the cover state the manufacture date is 2012. Also there are several stickers that say “Made in China” :(

Seems like a short service life as compared to the other American made AC units I have had.

From my research, it looks like I have lost the Freon charge? Is there anything else I should try before I replace the unit?

Thank you
  • A slight oily residue at the solder joints may just be left over flux from the original build.
    If the compressor is running then the caps are good.
    Probably time to get it looked at by a pro. I would not use a RV shop, they'll probably just automatically tell you to replace it.
  • I would have an AC service guy look at it.
    They can troubleshoot and add ports and freon if necessary.
    Might also get some help from Dometic.
  • Oil at the solder joints is not good.

    When the unit is running, touch the hi side copper tube leaving the compressor. It should be hot.
  • Fan runs
    Compressor runs

    Air flows out of ducts?

    Air is not cool when on AC or hot when on Heat pump?

    Then you have a leak and all freon is gone.

    Cheaper to replace unit then it would be to have tech locate leak, fix leak, add service valves, add freon