Yes, the LP pressure is too low. It should be adjusted to maintain 11.5” with most of the LP appliances going. In fact, I would try to adjust it for 11.5” with the furnace, water heater, and generator going. If it won’t adjust, you’ll need to replace the regulator.
Your regulator should be sized by the total btu’s of the LP appliances it’s supplying gas to.