Halffull's avatar
Halffull
Onan output wiring
I have a 6500 w Onan with 2 - 120 v 30 amp breakers. Is it possible to run the two legs to an electrical panel, then to a 240v to 120v step down transformer? My question is for two reasons. With only one leg being loaded, it seems to me that it's putting uneven pressure on the generator, and also the one breaker being used sometimes trips if the inverter is doing a bulk charge on the battery bank AND another heavy load kicks in.
  • I am not familiar with new Onan units.
    Do they have spec plaques designating 240/120?
    I can see center tapping a stator to obtain N and two Lines for a three wire output. In that case a transformer would be mandatory for single phase/neutral full nameplate output.
    At one time TRACE ENGINEERING sold a toroid 2/1 transformer rated 4 Kw. continuous 5 Kw surge. Very compact and significantly cooler (efficient). Check with OUTBACK company.
  • Chris Bryant wrote:
    Unless it is an old unit, or a commercial unit, your Onan is a 120 volt genset, both breakers come off of one single winding. Is your rig a 50 amp or 30 amp rig?
    As posted below, the generator is a year old and is used at a remote off grid fishing camp as backup to a solar/battery system.
  • You may well be correct, but my main point is that the units do not produce 240 volt power- on the schematics I looked at the windings all go to a common terminal, which feeds both breakers. It all depends on the model, though.
  • MrWizard wrote:
    Somebody wired your breaker box wrong? What is the main in your breaker box?
    Too much load on one side
    It is most likey wired with all your loads on one side including one air
    And the other side is only carrying the other air
    Yes it could be reconnected for 230v but you don't need too do that
    Just need to have a two line input breaker box, using both generator output lines
    And balance the load distribution
    The other question is the water heater on LP? What about the fridge?
    When In hot weather using the genset and air, making sure those stay on LP manually is a good idea, so they don't switch over and use the Onan power
    That Onan is big enough provided the loads are balanced
    The unit isn't in an RV, it's wired ONLY into a 120v 2500 w inverter/charger which is backup to a small solar bank.
  • Matt_Colie wrote:
    Without knowing the actual model number of the generator, we can not answer you. It is possible that it is two 30 amp line in phase and as such you don't have a 240 output, you have two 120V lines at 30 amps each. Onan has built all manner of machines.
    Matt
    The unit is new, model HGJAB-904
    Thanks
  • Chirs
    i have never seen a 6500 with only one winding
    all i have seen are (2) winding's wired in parallel
    some times tied together before the breakers sometimes not
    but always (2) winding's
    of course i haven't seen everything, ever done with Onans and RVs
  • Unless it is an old unit, or a commercial unit, your Onan is a 120 volt genset, both breakers come off of one single winding. Is your rig a 50 amp or 30 amp rig?
  • Somebody wired your breaker box wrong? What is the main in your breaker box?
  • Without knowing the actual model number of the generator, we can not answer you. It is possible that it is two 30 amp line in phase and as such you don't have a 240 output, you have two 120V lines at 30 amps each. Onan has built all manner of machines.
    Matt
  • Many older 6.5 NH Onans (1,800 RPM) have a terminal block inside the box with the breakers. If you know the wire numbers to reconnect the unit will deliver fifty amperes at 120 volts.
    I would LOVE to get my greasy hands on one of these units.
    With a WOOODWARD electronic governor to hold speed at precisely 1,800 RPM, these saturated field (self regulating) generators are near bulletproof.
Having RV issues? Connect with others who have been in your shoes.24,343 PostsLatest Activity: Dec 11, 2025