kerrlakeroo wrote:
I have seen several comments and ads for paralleling 2000 Honda generators. My question is why? a standard 4000 watt generator has 230 volt power available, so why screw around with 2 small generators and try to parallel them?
your RV does not use 230vac
RVs use 30amp 120vac service
or
a 50amp service which is (2) 120vac 50amp lines, aka (100amps at 120v)
you don't need or want 230vac
the 'inverter' style generators use less fuel and make less noise when at low power battery charging or watching TV
Champion makes qood equipment, you won't use 4000w unless you are trying to MW while the A/C is on, and that may not work if its too hot outside
A/C compressor surge is the biggest load any generator will see
even a large 1100 cooking watt MW only uses around 1600w input power
the lock rotor start up on a roof top A/C can be 54amps 120v
some newer A/C units use less power and have a lower start surge on the A/C compressor, the numbers you need to know are stamped on the metal plate on the A/C compressor, removing the cover and getting this info, is helpful to have around,