Forum Discussion
- MrWizardModeratoryou found it, you fixed it, and you have learned a 'lot'
good work
i remember thinking there was a reverse wiring connection
I thought it was in the extension cord,
you found it in the generator - 185EZExplorerThank you to everyone for being patient with me and helping out.
Beers on me
Stop on by
A Happy Camper - There should be no ill effects!
- wnjjExplorer II
185EZ wrote:
sunavabitch
That was it
I had to rotate the 30 amp outlet to make the wires reach but it also makes it easier to plug in the cord. The way they had it was difficult to plug in. I almost bought an adapter.
No more codes on EMS and it sent power through.
Would there be any damage to my rv when I had it plugged in directly to the generator with those wires switched?
Everything seemed to work fine
No harm done running it like it was. Without a ground bond, neutral and hot are arbitrary. It would only cause issues if some kind of device needed both 20A and 30A at the same time and shorted the neutrals together inside. Your bonding plug plus EMS RV was a harmless version of such a device. ;)
What you found explains everything which is why I posted this earlier:Tied inside makes sense, but what I meant was that the 20A receptacles selected one of the output legs as neutral and the 30A receptacle selected the opposite one.
Glad you have it all straightened out. - 185EZExplorersunavabitch
That was it
I had to rotate the 30 amp outlet to make the wires reach but it also makes it easier to plug in the cord. The way they had it was difficult to plug in. I almost bought an adapter.
No more codes on EMS and it sent power through.
Would there be any damage to my rv when I had it plugged in directly to the generator with those wires switched?
Everything seemed to work fine - Blue wire should be on silver screw!
- 185EZExplorerOne thing I noticed was the blue wire on the 15 amp receptacles is attached to the silver terminals but the blue wire is attached to the gold terminal on the 30 amp
the red wires are attached to the gold terminals on the 15 amp and attached to the silver terminal on the 30 amp
gen by 185 EZ, on Flickr - Optimistic_ParaExplorerI'd be opening that genny up and tracing the wiring to that 30 amp socket, personally. Something ain't right in there. You can't assume that just because something is new, that the factory didn't screw it up.
- 185EZExplorerquick recap
The generator works fine plugged into the rv without the EMS
The EMS is plugged in by itself to the generator and won't let current through due to an open ground
Plugged in the outlet tester to the 15 amp and 30 amp outlets and it shows open ground same as with the EMS.
Plugged in the bonding plug to the 15 amp outlets and the tester says it's correct or good with 15 amp outlets
But the 30 amp rv outlet shows hot/neutral reverse and the EMS shows code reverse polarity - road-runnerExplorer III
pnichols wrote:
Anything is possible until it's tested. I'll just say I've had 2 dometic fridges that didn't care about the bond, and I've never noticed a report of any RV fridge caring about it.
Could this be that the Norcold refrigerator's control board is sensitive to the little generator's output not having it's neutral bonded to it's ground ... as is being dicussed here?