- DrewEExplorer III
185EZ wrote:
wnjj wrote:
185EZ wrote:
I fixed the E2 open ground issue with a plug wired with the ground and neutral together.
NOW I have code E1 reverse polarity
I’m thinking you bonded ground and hot, not ground and neutral. Did you connect ground to the wider blade of the plug?
Wouldn't that trip the breaker?
Yes ground to silver wider blade
It would be nice to use the EMS but it's probably not best suited for generator use.
Bonding ground to the hot would not trip a breaker unless there is a (significant) ground/neutral fault somewhere else in the wiring, causing a short circuit.
On the generator itself, the whole output is floating (not bonded to anything), so neutral and ground are electrically interchangeable; it's just a question of which is wired to which blade of the socket.
If the EMS is saying reversed polarity, it means that it sees ground as at the same voltage as hot. This would mean either the bond is between the hot line and the ground, or the hot and neutral are getting switched around somewhere between the plug and the EMS (because something is miswired). Either way, whatever the problem is should be fixed. - 185EZExplorer
wnjj wrote:
185EZ wrote:
I fixed the E2 open ground issue with a plug wired with the ground and neutral together.
NOW I have code E1 reverse polarity
I’m thinking you bonded ground and hot, not ground and neutral. Did you connect ground to the wider blade of the plug?
Wouldn't that trip the breaker?
Yes ground to silver wider blade
It would be nice to use the EMS but it's probably not best suited for generator use. - TurnThePageExplorer
2oldman wrote:
This would be my solution too.
Bypass the EMS. Nobody grounds a generator. - agesilausExplorer III
MrWizard wrote:
Factory extension cord ?
Or one that has one or both ends replaced ?
Check the wiring on the replaced ends
Store bought and new. On one of the 120V outlets not the 30 amp. 4K generator. - 2oldmanExplorer IIBypass the EMS. Nobody grounds a generator.
- MrWizardModeratorFactory extension cord ?
Or one that has one or both ends replaced ?
Check the wiring on the replaced ends - agesilausExplorer IIIWell I made a plug with the green gnd screw and the silver neutral screw are connected with a short length of 12 gauge wire. It fixed the one amber light problem but then appliances at the end of the extension cords started shocking people.
Oddly using the tester at the end of the extension cord gave two amber lights before adding the plug. - wnjjExplorer II
185EZ wrote:
I fixed the E2 open ground issue with a plug wired with the ground and neutral together.
NOW I have code E1 reverse polarity
I’m thinking you bonded ground and hot, not ground and neutral. Did you connect ground to the wider blade of the plug? - 185EZExplorerI fixed the E2 open ground issue with a plug wired with the ground and neutral together.
NOW I have code E1 reverse polarity - 185EZExplorerIt's ok guys. Not worth getting into a tiff over it.
I got my answer and even a link to a part
Can't ask for much more than that.
Thanks to everyone! :)
BTW, which oil should I run in it?
Lol, JUST KIDDING!
About Technical Issues