Forum Discussion
Interex
Jun 19, 2017Explorer
DutchmenSport wrote:
If the breaker is tripping when you run the air conditioner, then either the breaker is NOT 20 amps, or else it's getting weak.
Another thing... if you have anything running on that same circuit in the house, lights, appliances, devices) anything in the house on that same circuit, you could easily exceed the 20 amps. Make sure absolutely everything on that circuit is turned off in the garage.
It's not tripping when it runs the A/C so I figured it's something to do with just the water heater.
Old-Biscuit wrote:
Tripping service breaker for garage outlet.......
WH element is 1440W and can pull 12--12.5 amps
Add in converter especially when charging batteries
PLUS anything else on that garage outlet circuit???
But element would have to be energized (in heat mode) otherwise NO amps
With CB immediately tripping......bad element.
At least with a Suburban it is right there under burner tube in outside compartment vs on backside of WH tank like Atwoods
Nothing else on the circuit. Since it trips as soon as I plug it in, I'm leaning towards a bad element.
Toddupton wrote:
Is the element bad in the water heater? Was it full of water while it was turned on or was it empty?
Water heater was full when I plugged it in.
MEXICOWANDERER wrote:
MANY water heater coil failures short to ground. Disconnect wire from element. Turn breaker on. Ta Dah! Black & White diagnostic.
I was reading about that. I may try that. Thanks!
eHoefler wrote:
Length of exstension cord and size with dramaticaly affect it.
I was only running the 30 amp cord with an adapter on the end.
j-d wrote:
You "brought trailer home for the first time"... Is this a new trailer, new to you, or one you've had and used awhile?
Really shouldn't trip a 20 with a less-than-15 load, even with converter running. Maybe if your House Battery was also low...
Is your 20A breaker a GFCI Breaker?
Maybe weak breaker...
My gut is, failing element, but it's that, a guess.
We have 15000 A/C and basically we can't run electric water heater in summer with its 30A service. I replaced the 1440W element with a 1000W and it lets me run it sometimes. I try to run it at off times. Like when campground voltage is high, and when we don't need to run something else.
It's a new trailer to me but only a year old. The 20a breaker is not a GFCI.
I'm going to take a look at the ground wires and see if I need to replace the element.
Thanks so much for everyone's input!