Roof air questions--now need motor info 5/6/14

Dometic 13,500. When I turn the AC on or only the fan on the coach, the breaker for the AC trips. Changed the breaker (20amp) and still the same. Cannot find anything wrong with any wiring. Fan is turning easy. Pulled the capacitors and did a check (test) I found online. They didn't check right--not sure if it's me checking or actually the capacitor.

Will a bad capacitor trip a breaker? If not, where else should I check?

Thanks
DICK
  • The only way a bad fan a capacitor would trip a breaker is if it is shorted to the case- an easy test. Just pull the wires and test for continuity between terminals and case.
    If it blows right away, it sounds like a dead short, or shorted fan motor. Either way, it's a matter of elimination- it could even be a short in the control box.
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    Will a bad capacitor trip the breaker? Possibly yes. HOWEVER this next statement is a YES, no doubt about it.

    IF the bad cap is the start cap, (Some motors have only a start cap, some start and run) then the motor will never come up to speed it will remain in "Locked rotor" mode drawing way more power than it normally draws and this will.

    1: Trip the breaker and 2: Burn out the motor over time.

    So either the bad cap tripps the breaker, or it causes the motor to do it, but either way a bad cap can make the breaker go CLICK.
  • Change the Capacitor and see if the A/C works. A bad capacitor will cause the AMP to spike on compressor start up.
  • Change the Capacitor and see if the A/C works. A bad capacitor will cause the AMP to spike on compressor start up.