BFL13 wrote:Continuous is defined as 3+ hours.
-The operating at 80% NEC guide/rule is for "continuous" (yes?) but the 1.25 over STC idea is for "occasional" times when the panel is doing more than its Voc /Isc at STC. So why can't the fuse etc be at just 1.25 too, not 1.56, since it is not expected to be running at 1.25 continually?
There is no 1.56%, only 1.25%.
For example a 40 amp continuous device needs to be on a 50 amp supply circuit including #6 wire and 50 amp breaker.
End of story.