For those interested. For not using voltage with LFP as a SoC here are examples from my system with 500ah GBS batteries/ EMS and a Magnum 3000 hybrid inverter. The system is 2 years of continual fulltime use and the past 460 days of boondocking with no hookups only the solar and a honda 2000 generator used for a hold over boost if needed on the third or fourth day of poor weather. The inverter is always on with a 2ah parasitic draw.
These are early morning readings before turning the coffee pot on (0630-0700) SoC and voltage from the Me-Arc display which only shows the voltage as xx.x vdc with 2a draw (inverter). 1%=5ah
32% 12.9
37% 13.0
41% 13.0
42% 13.0
54% 13.0
56% 13.0
58% 13.0
59% 13.0
63% 13.1
69% 13.1
74% 13.1
As can be seen there would be alot guessing used for SoC using voltage.
**13.33vdc is roughly resting voltage at 100%***
Now a couple using the actual display with readings from the EMS display which shows xx.xx vdc.
32% Inverter 12.9 2a, ems display 13.03vdc
74% Inverter 13.1 2a, ems display 13.26vdc
32% microwave/ inverting 12.5 150a after use the EMS display 13.03vdc
74% microwave/ inverting 12.9 150a after use the EMS display 13.17vdc
Example of the displays with 41a being drawn from the norcold fridge, tv charging laptop.