Just to clarify - is your desire to hook up to a 30a pole as well? Or, are you wanting to use adapters to run a 30a cable from a 50a pole?
The former, I would presume, would be fine if you don't have a call for the power. You don't want to run a 30a cable between a 50a pole and a 50a breaker, however, as the cord is not rated to carry that much power.
Good question......
I have a 50 to 30 amp adapter, so I would use the 50 amp twist lock on the camper to the 30 amp adapter then connect to the 30 amp recepticle in the power pole.
Is there an advantage to using the 50 amp power pole receptacle? Then I would need two 50 to 30 adapters?
Ron W.
You would be well advised to avoid putting in a 50A male to 30A female adapter at the power post, and then running a 30A cord which connects to your 50A RV, as there would not be adequate overcurrent protection for the 30A cord. This isn't quite the same situation as plugging a 30A RV into such an adapter since the RV main breaker provides protection for the cord under ordinary circumstances. (There are a few abnormal fault conditions where the cord could still be improperly protected, such as a short at the cord connection to the RV, but they are exceptionally rare, doubly so given the fault current would need to remain low enough to not trip the 50A breaker.)
Alternately, you could build (or may even be able to find) a 50A to 30A adapter with a 30A circuit breaker built into it, protecting the 30A cord that gets attached.
Sometimes the 50A receptacles in campgrounds are in better condition than the 30A receptacles, which is a decent reason to prefer that 50A receptacle.