lawrosa
Oct 12, 2017Explorer
BFL13 wrote:
Once you have the wiring such that the converter is maxed out, there is no point adding more wire unless you plan to swap to a higher amp converter in place. As you noted, you are getting the max amps now.
A few years ago, I decided to improve my 7355 converter (mid trailer) connection to the battery bank up front, since I could only get 25 amps or whatever at its 13.8v.
I ran a 20 ft length of copper water pipe under the trailer and wired it at each end to battery and converter to run in parallel with the frame on the neg side. Boom! Big increase in amps to battery.
Then I added a run of fat wire on the pos side in parallel with the existing pos wire. Boom some more! Using the 7355 as a power supply, not as a battery charger, I was now able to get 56 amps to the battery. Just for battery charging I was able to get more like 40 amps on that same pos and neg path instead of 25 amps. of course with that 13.8 single voltage converter, I was not able to test for amps to a battery at 14.4v.
So I am a believer in parallel DC wiring, but you can get it wrong. Eg, if one of the wires fails, the other should still have the ampacity to run the amps without melting. The one wire will have a huge voltage drop, but that is not melting. Different issue.
The idea is to have both paths in parallel take about half the amps, but they will actually do it in proportion, so you can have it where one is doing nearly all of it. In that case it might not be "worth it" to have the other one.
interesting..Id like to discuss this..
Well what I think is if I run the other # 6 , its similar to the #6 thats there now.. The factory #6 may have more strands and thicker jacket why they look different.
Actually the #6 I have is typical 600v AC wire I assume.. Its good for 75 amps @ 194F
I believe once that goes on the breaker I have that was linked above ( 100 amp) it will have similar resistance to the factory wire..
Ummmm,,,, now that I think about it maybe I should treat them seperatly and fuse each line?
The reason is I am not an electrician. Im a plumber 35 years.. If as you say one line faults it may not trip that breaker. The wire may burn before the breaker trips.. FIRE!!!!! lol
I think I am best off putting a 40 amp breaker or 50 amp on each line...
Easy to do.... and cheaper for me as I have the wire..
If I had to buy wire to try to increase the size I dont think I would gain as much as I did when I paralleled them...
What do you think? Because the specs for the wire are as so..
Type THHN or THWN-2 conductors are primarily used in conduit and cable trays for services, feeders, and branch circuits in commercial or industrial applications as specified in the National Electric Code
When used as a type THHN conductor it is suitable for use in dry locations that are not to exceed temperatures of 90ºC
THHN copper conductors are annealed (soft) copper
Heat-, moisture-, gasoline- and oil-resistant
But what I see online it shows it makes no difference as long as it carry's the amps...
and both #6 wires will carry the amp rating of the converter if one fails...