ktmrfs wrote:
I'd go with the GC IF your typical current draw is reasonably low like 25A or less. This sounds like your case.
If you typically are going to run an inverter with a heavy load (>75A), then the 12V may work better.
GC have an advantage of having very high cycle life even down to 30% SOC or more, (hundreds of cycles) taking abuse as long as they are kept watered and properly charged etc. However, every battery design has tradeoffs, and with GC it high load current. They have fewer but thicker plates so they have higher internal resistance which compromises high current use.
Since you can repeatedly draw GC down to 20-30% SOC and still get hundreds of useable cycles, the GC wins in the "useable" AH category compared to a 12V. For example a 12V combo of 250AH has realistically 125 Useable AH at 50% DOD, the max recomended for most 12V batteries. By comparison, a 250AH bank of T-125's will give you 250*.7= 175 "useable" AH, That "extra" 50AH could give you an extra day or two of camping.
My last set of Trojan GC were quite often discharged to about 30%SOC, probably about 20 times/year and 50% another 30 times year. After 8 years they went to in-laws and are still running strong for him, better than his bank of 3 year old 12V by far. SG after 8 years is still 1.275 on each cell.
Another thing is how often will you boondock?? If it's only a few times/year, 12V may end up being the lowest cost/year choice. If in a pinch not worrying about discharging the batteries down to 20-30% SOC is important, then GC win hands down. The trojan GC have a higher cycle life at 30% SOC than the trojan true 12V deep discharge do at 50% SOC.
But in either choice the key to longevity is getting a quality battery and properly recharging them as soon as you return from a trip. And unfortunetly, the common WFCO charger in many trailers will seldom do anything near a proper recharge since they seldom go above 13.6V. And you need to get into the 14.5+ V range to properly recharge a flooded cell battery. So you need an iota or Progressive dynamics charger or better yet, the B&D Vector portable charger to get them recharged.
This post has opened my eyes to something that should have been obvious. There is a mismatch between 6s and inverters for two reasons:
- they have a large voltage drop under high amp draw
- the inverter has an 11v loaded voltage alarm you try to stay above.
Which means you can't exploit the advantage of 6s in going to a lower SOC to get more AH before you need to recharge them.
Using the 12s for inverter matches in that you want to stay above 50
% SOC anyway, so the inverter alarm is not itself a restriction on your DOD, and the 12s have less voltage drop under high amp draw, so you can get away with those inverter loads longer.
I am currently trying out a new arrangement with the big inverter on my 12s and the small inverter for TV etc on the 6s with the rig on the 6s too for furnace etc.
But the quoted post has just hit me that I am missing a trick here, by not putting all my inverters on the 12s, leaving the furnace etc on the 6s.
It is possible with some juggling that would allow the 6s to go longer to 30% before a recharge is needed and that the 12s would still be good at 50% till then too, if the AH draw from inverter use was managed right. That would depend on a whole bunch of situational things of course.
Some other folks here have a mix of 6s and 12s, so it might be worth a look.
(BTW, my 12s are Trojan golf car batts (T-1275s) so I find the quoted post confusing. I don't know if they come under the not below 50% rule or not. They do have less voltage drop than my 6s under high amp load though, so that part of being 12s applies ok.)
EDIT--now I am wondering about any advantage in putting the pair of 12s as a 24 and using a 24v inverter, since there is no "ordinary" rig draw on the 12s. My solar controller will do 24 batts or 12v batts too. Hmmmm. But I don't have a 24v inverter.