ktmrfs
Oct 09, 2015Explorer III
It's against NEC code for the trailer to have neutral and ground bonded together. Neutral/ground bonding is ONLY allowed at the main feed breaker panel, nowwhere else down the line. The main feed panel is either the panel in your house, or the panel at the CG. The trailer is just like another thing plugged into a wall outlet, neutral/ground bonding prohibited.
If you open up the pedestal at a campground, I suspect you would also find that at the pedestal neutral and ground are not bonded either. the neutral bus bar is likely insulated from the metal housing. At least that is what NEC code will want.
In fact, if the trailer has a neutral/ground bond an upstream GFI will trip and not supply power since newer GFI will trip either on a hot neutral imbalance or a neutral/ground bond.
One can come up with all kinds of cases where trailer neutral/ground bond will be dangerous or protect you. Likewise without a neutral/ground bond.
However, I'll leave it to NEC to decide what is best, and they say not allowed.
now this does cause an issue with those of us using a portable generator with an EMS system that will shut down with an "open" ground, which is what it will detect since a portable generator in compliance with NEC as a portable device doesn't have a neutral/groud bond. There are mutliple solutions, one common one is a plug with the neutral side shorted to the ground side and plugged into one of the outlets on a duplex outlet, thereby making the EMS think there is a neutral/ground bond.
This condition does not apply to most onboard generators because they usually do have a ground/neutral bond with the generator being the main power source.