60 Amp is too big for the #8 wire you have running to the barn. That should be a 40a double-pole breaker at the source. I believe that NEC requires a disconnect for all sub-panels so you should have a 40A double pole as the "main" in the barn, then a 30A double pole for the RV plug and a 15A single pole for the light circuit.
Somebody please chime in if this is not correct.
Somebody please chime in if this is not correct.