enblethen wrote:
The inverter constitutes a derived service and should follow the requirements of NEC Art 250-30.
How does the inverter instructions say about how to wire the system. I believe it will say not to connect them together!
I still say the easiest is to extend the one branch circuit to feed straight off inverter. No overcurrent protection required, no chance of back-feeding and very easy to do.
Enblethen, this would require creating a sub-panel that the inverter feeds into, right? Do you think that's easier than having the inverter feed into half (one leg) of the existing panel?