Forum Discussion
time2roll
Oct 17, 2019Nomad
joe6789 wrote:NO. My original comment was a reply on your suggestion to have two neutrals with one of the neutrals not going through the inverter. As shown in the diagram the single neutral goes through the inverter and all is good and properly switched.time2roll wrote:
Yes. This is same as we discussed earlier.
Single phase 120v will feed L1 & L2 and close the relay for normal operation on 30 amp service.
Thanks Time2roll. Let me follow up on something you said earlier:
"I believe Neutral needs to be switched during inverter operation to prevent back feeding"
How does that relate to the above diagram from Victron? Do you think an extra transfer switch needs to be added, or do you think the Multiplus will safely handle it on its own?