bjarnold wrote:
It's a 2007 and the model is GC6AA-10E. I cleaned the terminals on the circuit board and I have 13 volts coming into the circuit board via the orange wire on the top plug
OK this helps greatly knowing you have the newer control system.
You said this"
bjarnold wrote:
Atwood gas/electric water heater with DSI and it works fine on electric but does not work on gas. The gas valve does not open, the ignitor does not fire, the red light on the switch panel does not light up. I bypassed the thermostat and still doesn't work.
On that newer unit, the control board runs both the gas and the electric relay to the electric element. The safeties are working for both. Meaning, if it works on electric, then the T stat and the Thermal fuse are or were working.
Your's does have the thermal fuse. Or at least the part number shows it does. This is a small resistor looking deceive that is normally plugged onto the terminals of the T stat with a clear tube cover and and then the brown wire on the end of it goes back to the control board. The thermal fuse is called "thermal cut off" in Old Biscuit's diagram.
Have you tried this back again on electric? OR do a voltage check on the control board pin that has the brown wire from the thermal cut off fuse that goes back to the control board. Do this at the board so you know the safety circuit is in tact. Point being, need to make sure you did not make the safety circuit not work by fiddling with the wires. Easy to do.
If it works on electric and it does not work on gas, and while on gas it does not start the ignition (click, click, click) and no loud clunk of the gas valve, you "might" have a PC board issue.
The board sends ignition signal through the hi tension wire. And the board sends the 12 volts to the ECO switch and the gas valve.
If the board has 12 volts going in the orange wire, means gas mode, and the safety circuit is working, the only thing left is the control board. It would be odd that both the gas valve and the igniter would die at the same time but not impossible. You can put a volt meter on the gas valve and ECO wiring and look for 12 volts but the gas valve makes a load clunk when they engage. You can hear it if you are outside and someone turns on the gas switch inside.
Atwood service centers should have a board tester to tell you if it is bad.
Hope this helps
John